Hello - I am wiring a hot in Maryland and we are on the 2014 code. I would like to be able to use LFNC about 12' to the panel box and about 6' before the disconnect outside and pvc in between. From what I understand as long as I strap it accordingly I should be fine. I thought at one time I remember hearing you couldn't use more then 6' . Thanks
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Hello - I am wiring a hot in Maryland and we are on the 2014 code. I would like to be able to use LFNC about 12' to the panel box and about 6' before the disconnect outside and pvc in between. From what I understand as long as I strap it accordingly I should be fine. I thought at one time I remember hearing you couldn't use more then 6' . Thanks

Wiring a "hot" what in Maryland?:p

As long as the LFNC is type "B" and you secure it according to 356.30 you can do it.
 