Customer wants a hot tub installed.
Manufactor calls for #8 thhn wire for ungrounded conductors, grounded conductor and EGC, a dedicated 50 amp circuit ( Hot tub name plate 230 v 40 amp)
The customer wants it in a garage, there's a few issues with the spot:
- right above it there's a garage door opener pluged into a recp.
-Above and 2 feet to the left there's a 2 bulb fluorescent light fixture.
-Above hot tub there's the rails for garage door
After talking inspector he told me that he doesn't require the concrete pad in the garage to be bonded but he will require the rails bonded.
As for the garage door opener recep., he tells me to take recep. out and put a blank cover on it.
Ok here's my questions:
1- Do you all agree on the garage door rails having to be bonded?
i would think they are not likely to get energized, and so be left out of the requierement.
2- Would that blank be enough?
3- I was thinking about removing fluorescent fixture and be done with it.
or install an adequate fixt. if customer desires.
4- since i need #8 EGC from the panel to subpanel, does #6 w/ground have a #10 or #8 EGC. ( I'll be using NM from panel to subpanel)
Thanks.
Manufactor calls for #8 thhn wire for ungrounded conductors, grounded conductor and EGC, a dedicated 50 amp circuit ( Hot tub name plate 230 v 40 amp)
The customer wants it in a garage, there's a few issues with the spot:
- right above it there's a garage door opener pluged into a recp.
-Above and 2 feet to the left there's a 2 bulb fluorescent light fixture.
-Above hot tub there's the rails for garage door
After talking inspector he told me that he doesn't require the concrete pad in the garage to be bonded but he will require the rails bonded.
As for the garage door opener recep., he tells me to take recep. out and put a blank cover on it.
Ok here's my questions:
1- Do you all agree on the garage door rails having to be bonded?
i would think they are not likely to get energized, and so be left out of the requierement.
2- Would that blank be enough?
3- I was thinking about removing fluorescent fixture and be done with it.
or install an adequate fixt. if customer desires.
4- since i need #8 EGC from the panel to subpanel, does #6 w/ground have a #10 or #8 EGC. ( I'll be using NM from panel to subpanel)
Thanks.