I've always been taught to have a disconnect "readily accessible" to the users of the hot tub. I've also been taught that the feeders to the hot tub must be in conduit and must have an insulated ground from the panel to the disconnect. It all makes sense,
However, after boning up on my code some more, I noticed art. 680.41, last sentence, "this requirement shall not apply to single-family dwellings.
And art 680-42(C) states "that contain a copper equipment grounding conductor that is insulated OR enclosed within the outer sheath of the wiring method.....shall be permitted to be used for the connection to motor, heating and control loads..."
Would this mean for a single-family dwelling, I can use 6-3 romex, no condiut. I'm thinking now though, what type of breaker would I use. Not sure if they make a 2p-50a gfci breaker, and if they do, it is probably cheaper to put a disconnect in.