We ran (2)#12 from 20A/2P breaker in panel to serve a remote 208V/1PH, 10A motor. (motor is 120 ft. from panel)
It turns out the motor is actual 120V/1PH.
Instead of re-run #12 Hot, #12 Neutral wires to motor, can we still use above 2#12 wires and land it on 20A/1P breaker in panel but tag one of #12 wires with grey/white color tag and consider it as neutral wire? Thank you!
200.6 prohibits doing so.
(requires the jacket to be "continuous color" on wires #smaller than #4.)
200.6 Means of Identifying Grounded Conductors. (A) Sizes 6 AWG or Smaller. An insulated grounded conductor of 6 AWG or smaller shall be identified by one of the following means:
Changed From 2008
200.6(A): Editorial revision of existing information into a numbered list.
(1)
A continuous white outer finish.
(2)
A continuous gray outer finish.
(3)
Three continuous white stripes along the conductor's entire length on other than green insulation.
(4)
Wires that have their outer covering finished to show a white or gray color but have colored tracer threads in the braid identifying the source of manufacture shall be considered as meeting the provisions of this section.