Electricalhelp
Senior Member
- Location
- NJ
The incoming service is 120/208V/3P.
The Hot Water Heater says it's Input KW is 40.5kW-120/208V/3P
So please let me know if I am doing the path correctly
40500/1.73*208 = 112.42 Amp
112.42*125% = 140.52 Amp
So will I require a 150 AMP since a water heater of this type is required to be considered a continuous load meaning that the branch circuit needs to be calculated at 125% of the heater’s rated ampacity.
The Hot Water Heater says it's Input KW is 40.5kW-120/208V/3P
So please let me know if I am doing the path correctly
40500/1.73*208 = 112.42 Amp
112.42*125% = 140.52 Amp
So will I require a 150 AMP since a water heater of this type is required to be considered a continuous load meaning that the branch circuit needs to be calculated at 125% of the heater’s rated ampacity.