hi,
I am wiring up a insta hot. The name plate states 240V/13000W
We have a 208V three phase system should the calculation be based on 208V
13000/208V=62.5 * 1.25 = 78.125Amps?
The calculation you use would be correct for a motor load run at full power from either voltage. But that is not what you have.hi,
And the 25% reduction in wattage probably means that the water will not get hot enough.
There is a quicker way. Since power is V*V/R, and since R is constant, you get the new value of power by taking (208/240) squared, and multiplying that times the original 13000 watts. There is an even quicker way, and Don hinted at it. Running a 240 volt rated resistive load at 208 volts gives you a 25% loss of power (208/240 squared is 75%).You have to calculate ohms and then use ohms law to solve at 208V