Hot Water Heater Disconnect?

Status
Not open for further replies.

mdshunk

Senior Member
Location
Right here.
frogneck77 said:
Anyone hear of a code requirement for a disconnect on a hot water heater?
You betcha. Within sight and within 50 feet. Sometimes the breaker in the panel is sufficiently close to qualify.
 

electricman2

Senior Member
Location
North Carolina
Occupation
Retired Electrical Contractor
stickboy1375 said:
Yeh, its an appliance... :grin: And its not a hot water heater, if the water is already hot then there is no need to heat it.. :) sorry I couldn't resist...
Sure you could, you just didn't;)
 

frogneck77

Senior Member
Location
Shelton,CT
stickboy1375 said:
Yeh, its an appliance... :grin: And its not a hot water heater, if the water is already hot then there is no need to heat it.. :) sorry I couldn't resist...
I knew I would get the usual treatment for asking a dumb question, but I couldnt help it. In the 13 years Ive been wiring houses Ive never had to install a disconnect on a Cold water heater.Conversing on this forum helps me take my brain out of autopilot quite often-Thanks for the laughs and all the great info-I really respect all of your opinions,the occasional spark of wit is entertaining as well
 

stickboy1375

Senior Member
Location
Litchfield, CT
frogneck77 said:
I knew I would get the usual treatment for asking a dumb question, but I couldnt help it. In the 13 years Ive been wiring houses Ive never had to install a disconnect on a Cold water heater.Conversing on this forum helps me take my brain out of autopilot quite often-Thanks for the laughs and all the great info-I really respect all of your opinions,the occasional spark of wit is entertaining as well


I'm not smarter than anyone else, and never feel a question is a dumb one...
 

frogneck77

Senior Member
Location
Shelton,CT
Ill admit it, Im one of those guys who doesnt pull the code book out very often.I still reference the 2005 in a pinch because thats what I took my E1 and E2 tests on. I come on to this forum to brush up on code and ask questions about anything that comes up in my day I think you guys can help me with. You guys rarely disappoint,w/info and laughs
Bill
 

stickboy1375

Senior Member
Location
Litchfield, CT
Minuteman said:
Some never miss an opportunity to crack wise.

I like breaker locks a whole lot better than installing a small disconnect (Or I have seen some install a 3 wire dryer outlet).

I highly doubt a cord on a water heater is legal...
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
stickboy1375 said:
but what do I know?

We all what to know the answer to that question. :grin:

I would bet anything it is an electric water heater- So there you at least know as much as I do and for your sake I hope you know more.:grin:
 

mdshunk

Senior Member
Location
Right here.
Minuteman said:
(Or I have seen some install a 3 wire dryer outlet).
I've seen that too, but that's not legal. A 3-wire dryer rec is 120/240 ungrounded, and for a water heater you'd need a rec for 240 grounded.
 

iwire

Moderator
Staff member
Location
Massachusetts
mdshunk said:
I've seen that too, but that's not legal. A 3-wire dryer rec is 120/240 ungrounded, and for a water heater you'd need a rec for 240 grounded.


I do not undestand.

What code would you cite?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
mdshunk said:
I've seen that too, but that's not legal. A 3-wire dryer rec is 120/240 ungrounded, and for a water heater you'd need a rec for 240 grounded.

Marc, what difference would that make. Isn't the 3 wire dryer ground terminal grounded to the metal of the receptacle?
 

stickboy1375

Senior Member
Location
Litchfield, CT
mdshunk said:
I've seen that too, but that's not legal. A 3-wire dryer rec is 120/240 ungrounded, and for a water heater you'd need a rec for 240 grounded.


I would go with that the Water heater is not listed to be cord and plug connected... :wink:

422.16 Flexible Cords.
 
Last edited:

iwire

Moderator
Staff member
Location
Massachusetts
stickboy1375 said:
I would go with that the Water heater is not listed to be cord and plug connected... :wink:

422.16 Flexible Cords.

I don't think Marc was talking 422.16.

BTW are you sure they are not listed for that, or like me you just never did it that way?

Insta-hots are solder in place and have cords. :smile:
 

480sparky

Senior Member
Location
Iowegia
Dennis Alwon said:
Marc, what difference would that make. Isn't the 3 wire dryer ground terminal grounded to the metal of the receptacle?

Technically, it is for the grounded conductor, not the grounding.

This is for 120/240:
nema_10-30p.gif






This is for 240:
nema_6-30p.gif
 
Last edited: