J JoeNorm Senior Member Location WA Jun 18, 2024 #1 Is it safe to assume 10-2 will cover all water heaters? Do some of them require a neutral? I have been roughing in with 10-3 because I haven't been sure but wondering if it is a total waste.
Is it safe to assume 10-2 will cover all water heaters? Do some of them require a neutral? I have been roughing in with 10-3 because I haven't been sure but wondering if it is a total waste.
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Jun 18, 2024 #2 10/2G 10/3 is a waste. I’ve never seen a neutral required.
E Eddie702 Licensed Electrician Location Western Massachusetts Occupation Electrician Jun 18, 2024 #3 Some water heater coming through with 5,5kw elements but 10/2 still covers that @240 volt. Used to use 10/3 around here when they used the switch in the meter for peak/off peak.
Some water heater coming through with 5,5kw elements but 10/2 still covers that @240 volt. Used to use 10/3 around here when they used the switch in the meter for peak/off peak.