ok just another simple question. A work mate (plumber) asked me what size wire and ocpd to hook up to a hot water heater. i'm thinking ok 10awg and 30amp, then he says 5500w 240
so i calculate 5500/240= 22.92 times 125% and get
28.65, so im in a small quandry. is it still 30 amp breaker or do i use the 80% rule and go 35amp breaker with 8awg wire. thanks for the help.