Good Morning
If you have a 80 gallon electric hot water tank @ 208 volts with two elements @ 4500 watts a piece non simultanious. do figure the amps @ 4500 watts or 9000 watts.
Thats why I questioned it.yes they run in open delta format with this set up and keep in your mind the B phase will have higher current drawage if both elements are on.
The OP says it's an 80...Nobody mentioned the size, as far as I know, that's what determines it, not the thermostat.
A WH less that 125 gallons in considered continous duty.
A wh more than 125 is considered non continous.
4500 watts, continuous, makes you run a #10 for the load
A WH less that 125 gallons in considered continous duty.
A wh more than 125 is considered non continous.
I believe it's 450 L (120 gal).![]()
A small distinction but I do remember a post from a while back where someone had come across a water heater on a job that was something like 121 gallons and thought it was a odd number.
But apparently it was manufactured with 422.13 in mind, so that it just crossed the threshold into non continuous.
Had a similar situation recently. I checked out the Rheem site and found this http://globalimageserver.com/fetchDocument.aspx?id=7522ff8d-b9a6-420d-ba77-3263d7148f76. (check out pages 8 and 20 of this PDF) The heating elements are interlocked so that they can't both operate at the same time. In my case I had (2) 4500 watt elements, non-continuous with a 3 wire outlet. Customer currently has a 2-pole 20 amp circuit to the heater that the plumber installed (replaced). It won't pass inspection and I've already told them they'll have to replace the wiring and disconnect. Will the wiring burn up before they decide that I'm right.Who knows
![]()
If it's 240 volt,and non continuous, the 20 amp circuit is big enough
Not the way I read the chart. It requires a 25 amp circuit so the next highest trade size breaker is 30 amps and # 10 wire. If you do the math 4500/240= 18.75 amps. 80% of a 20 amp breaker is 16 amps so you'll have to go to the next size up the way I see it.If it's 240 volt,and non continuous, the 20 amp circuit is big enough
Not the way I read the chart. It requires a 25 amp circuit so the next highest trade size breaker is 30 amps and # 10 wire. If you do the math 4500/240= 18.75 amps. 80% of a 20 amp breaker is 16 amps so you'll have to go to the next size up the way I see it.
Not the way I read the chart. It requires a 25 amp circuit so the next highest trade size breaker is 30 amps and # 10 wire. If you do the math 4500/240= 18.75 amps. 80% of a 20 amp breaker is 16 amps so you'll have to go to the next size up the way I see it.
I'm not talking about the chart. I'm talking NEC. The op said non continous.
Why can't I load a 20 amp breaker past 16 amps? Pleaase provide code article.