For hotel rooms without cooking,

1) How are the rooms treated in terms of receptacle load calcs, same as a commercial building or a dwelling?

2) Receptacle placement follows the same as dwelling units?

3) Are lighting circuits required to be separate than receptacles?

Working on a hotel guest room with adding new receptacles and lighting and want to make sure I can connect these to the existing circuits, shouldn't be a problem right?

Although wondering if adding new lighting, would that trigger a new energy code and all the control requirements with the master light switch at the entry?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
See 210.60 (A) & (B), 210.70 (B), and 220.14 (H). Those sections are from 2011 because that's what is in front on me.
 

cppoly

Senior Member
Location
New York
Thanks.

So hotels without cooking are still treated as dwelling units in terms of receptacle placement and calculations?

Except instead of 3 VA / SF, it's 2 VA / SF.
 