When sizing a service for a hotel with multiple suites (each with 3-circuts) and a 2p circuit brekaer for room a/c no stove or cooking appliances (maybe a microwave) can you treat each suite as a dwelling and apply demand factors as indicated in table 220.84 (demand factor for three or more multifamily dweling units.) or would you use the tables that indicate loads by occupance 220.12 va/per square foot? I have seen different engineers calculate it in different ways using 220.84 and 220.12 I believe that 220.12 is the correct way? is this correct?
One project constited of suites containing cooking equipment (range, microwave etc.) along with the general circuits, a 1 phase load center located in each suite and the total load computed using the table in 220.84 but this is a hotel and not a dwelling unit so is this correct to calcuate it this way?
What about hotels with no cooking provisions could you use tabel 220.84 or would that be incorect in calcuating the loads and 220.12 apply?
Thanks in advance.
One project constited of suites containing cooking equipment (range, microwave etc.) along with the general circuits, a 1 phase load center located in each suite and the total load computed using the table in 220.84 but this is a hotel and not a dwelling unit so is this correct to calcuate it this way?
What about hotels with no cooking provisions could you use tabel 220.84 or would that be incorect in calcuating the loads and 220.12 apply?
Thanks in advance.