Sierrasparky
- USA
- Electrician ,contractor
I am wondering if I am calculating a hotel HVAC load correctly?
I assume you take the heating or the cooling load which ever is greater.
In this case the heating load is actually greater because it is all resistant heat.
There are 75 rooms and each quest room has a 3kw electric heater.
According to :
220.51 Fixed Electric Space Heating. Fixed electric
space-heating loads shall be calculated at 100 percent of
the total connected load. However, in no case shall a feeder
or service load current rating be less than the rating of the
largest branch circuit supplied.
I take it this means that the electric heating load calculation is in added on top of all other loads or reductions.
OR is this type of load lumped into the entire load and then subjected to the various reductions as in Table 220.42
According to :