Governed under article 440 or 422? Air conditioning equipment or appliance.? Trying to determine rules for disconnecting means. 277 V. Thanks.
Was thinking if it fell under 422 a breaker lock would be permitted, or if under 440, within sight .Is there a difference in the requirements of those two articles?
These are normally cord and plug. Not sure I have ever seen a PTAC that is not cord and plug. The key is for 277 volt to meet NEC you must use the sub base. The recep. in the sub base is your disconnect.No. There‘s not one outside the unit. I have not opened one up yet. Just wanted to verify if disconnecting means would have a plug in the unit or if it would be permitted to be a breaker lock.
Thank y’all for the heads up.These are normally cord and plug. Not sure I have ever seen a PTAC that is not cord and plug. The key is for 277 volt to meet NEC you must use the sub base. The recep. in the sub base is your disconnect.