I am working on a hotel with ~100 rooms each with their own PTAC (3.1kW electrical back-up). They are controlled with a thermostat and occupancy sensor, and normally run in heat pump mode (7.3 running amps). Is there any demand factor I can use to lower my service size? Can I size the OCP and conductors per the 3.1kW and and use the 7.3A load for my service size calcs? The AHJ is not allowing me to call them dwelling units (I tried).
Thanks for any/all help