B bwyllie Senior Member Location MA Jan 11, 2006 #1 When doing a load calc on a hotel, do I add 2va/sf + 1500VA for a bathroom circuit and apply the approriate demand as per 220.42 and then add any HVAC units load? Thank you.
When doing a load calc on a hotel, do I add 2va/sf + 1500VA for a bathroom circuit and apply the approriate demand as per 220.42 and then add any HVAC units load? Thank you.
B bphgravity Senior Member Location Florida Jan 11, 2006 #2 Re: hotel room calcs Looks good to me. Don't forget the hall lighting or any other common area lighting are continuous loads and have different va/ft? allowances.
Re: hotel room calcs Looks good to me. Don't forget the hall lighting or any other common area lighting are continuous loads and have different va/ft? allowances.