Hotel Service and sub panel Question

Status
Not open for further replies.

shanebdx

Member
I am installing a 1600 amp 120/208 3 phase 4 wire main distribution panel in a hotel. The engineer speced out all the sub panels to be 120/240. There isnt any equipment that is 208 volts in the building. So why do they want a 120/208 3 phase main???
 
I am installing a 1600 amp 120/208 3 phase 4 wire main distribution panel in a hotel. The engineer speced out all the sub panels to be 120/240. There isnt any equipment that is 208 volts in the building. So why do they want a 120/208 3 phase main???

probably all the poco will give him at that size
 
probably all the poco will give him at that size
Right. They probably don't WANT a 120/208 service. That's probably all they can get. Having said that, I have no idea why a hotel would WANT 120/240 subpanels. Seems like a waste of a transformer. I wouldn't think they'd have any critical equipment that couldn't also run on (or be spec'd for) 208.
 
by 120/240 panel, are we talking about a 120/240 panel, or a 120/208 single phase panel? This is a big difference to clarify.

If you have 240vac only loads (because someone got a deal on some airconditioners) seems like it would be most cost effective to have 120/208 3ph panels for the 120v loads, then use 208-240 delta/delta transformer with 240v delta panels for the 240 loads...smaller transformer(s) and keeps everything balanced. Maybe someone who is more knowledgable about this can chime in....
 
By having a 3 phase 4 wire MDP and all 120 /240 subs, will the loads be distributed at the MDP without overloading?
 
That's easy. The maids have to go around with their voltage collection buckets every day and clean up the floors of the electric room. How could you not know that? :roll:

But how do you keep that 32 volts in the receptacles from leaking all over the building?
 