House and Garage on Seperate Service with Three Way Switches

Status
Not open for further replies.

al

Senior Member
Location
Minnesota
If we have a house and detached garage on seperate services is there any way to have three way switches at each and be code compliant?
 
Just to be sure ,.. there are two separate POCO service drops or laterals for this property ??

225.37 Maybe ??
 
Last edited:
Feed the three-way switches at the garage. This will work as long as the garage is sub-fed from the house. If there are two separate services (one for the house and one for the garage) see M.D.'s post for a possible solution.

Pete
 
M. D. said:
Just to be sure ,.. there are two separate POCO service drops or laterals for this property ??

225.37 Maybe ??
225.37, Exception 2 does not exclude with separate services, so it looks like no plaque is needed.
 
Reply

Reply

The garage is tapped off the load side of the meter. Thanks for the X10 suggestion.

Al
 