House Generator

Status
Not open for further replies.
While strolling through Harbor Freight I noticed an enclosed 9500 inverter generator. As I inspected the generator for power outlets, I noticed there are (2) two-pole 30 amp twist lock outlets. My question is, can the outlets work in tandem to create 60 amps of power to a residential electrical panel in situations where there is a loss of power. I know several electricians who use smaller generators with (1) 30 amp outlet and a manual transfer switch to power certain circuits during periods where the power is out. My thinking is that if (2) 30 amp outlets are working in conjunction with one another, more circuits could be energized when the power is out. Is my logic correct? Is this a safety issue that would cause damage to the generator or the electrical panel?

thanks!
 
I suspect one of those 30 amp receptacles is 120v because 60 amp at 240v is 14,400 watts. I realize this doesn't change the load on one leg but my guess is it's one or the other. They must assume you are not loading it up.

Either way I can't see how it can work as one breaker would trip if you went over 30 amps
 