dvcraven0522
Member
- Location
- St. Louis, Missouri
- Occupation
- Engineer
I have a 200amp house panel with FP tap. Inspector in requiring the service to the house must be 400amp. I agree with him.
My question does anyone have a solution in lieu of busting up concrete and running new conduit/wire. See attached one line. I suggest a shunt trip the main in the house panel in the event the FP comes on but contractor tell the lead times are 30 weeks.
I cannot run parallel feeders large enough in the exiting 2-1/2' pvc for 400amps.
Cost 30k to fix each location. This occurs on the 3 building.
Thx
Dan Craven
My question does anyone have a solution in lieu of busting up concrete and running new conduit/wire. See attached one line. I suggest a shunt trip the main in the house panel in the event the FP comes on but contractor tell the lead times are 30 weeks.
I cannot run parallel feeders large enough in the exiting 2-1/2' pvc for 400amps.
Cost 30k to fix each location. This occurs on the 3 building.
Thx
Dan Craven