250.140 How do clothes dryers pass UL listing with the nuetral conductor bonded to the frame and that connection is not accessable? Ranges have a visible copper strap and instructions for 3 or 4 wire cords. I have seen many clothes dryers wired with a 4 wire cord and the bonding jumper still attached to the green frame screw, (cord installed by appliance delivery boys:grin: ). The manufacture instructions that I have read do not say to remove the green wire from the screw. Am I missing something or what is the proper way to install a 4 wire cord? I always remove the jumper wire from the green frame screw, tape the end and stuff it back up in the dryer and hope the tape never comes off! I used to clip the green wire off where it is crimped on the the white wire, but that is seldom accessable.