I have had several instances lately where clients have called with complaints about their household ranges not operating. In all cases I found that the homeowners had replaced their older ranges with a newer and fancier ranges. In all cases the original ranges were 8kW to 9.6kW (33A to 40A) and were supplied from 40A breakers via #8 conductor cables. Also, in all cases, the newer ranges were 12kW to 13.8 kW (50A to 57.5A). In most cases, the 40A breakers just kept tripping however, in one case, the 40A breaker melted.
Rewiring for the newer ranges has presented me with some dilemmas that I would like some assistance in resolving. I know that 2002 NEC 422.10A, last paragraph, states that branch circuits shall be permitted to be in accordance with Table 220.19 (Demand loads). However, 422.10A, first paragraph, states that the branch circuit rating shall not be less the marked rating of the appliance.
Take the case of the 13kw range (54.2A). Clearly from the 2002 NEC Table 310.16, a supply cable with #6 conductors is required and may be protected by a 60A breaker (NEC 240.4B). If the range is to be plug connected and the range cable, plug and receptacle are rated at 50A are these parts acceptable for use?
What should be circuit configuration for a 13.8kW range (57.5A) consist of? Should it be hard wired with #4 conductor cable and a 60A breaker? That would certainly provide the necessary current carrying capacity.
I welcome any assistance.
Rewiring for the newer ranges has presented me with some dilemmas that I would like some assistance in resolving. I know that 2002 NEC 422.10A, last paragraph, states that branch circuits shall be permitted to be in accordance with Table 220.19 (Demand loads). However, 422.10A, first paragraph, states that the branch circuit rating shall not be less the marked rating of the appliance.
Take the case of the 13kw range (54.2A). Clearly from the 2002 NEC Table 310.16, a supply cable with #6 conductors is required and may be protected by a 60A breaker (NEC 240.4B). If the range is to be plug connected and the range cable, plug and receptacle are rated at 50A are these parts acceptable for use?
What should be circuit configuration for a 13.8kW range (57.5A) consist of? Should it be hard wired with #4 conductor cable and a 60A breaker? That would certainly provide the necessary current carrying capacity.
I welcome any assistance.