ronaldrc said:
Larry
How can I draw 100 amps. from line #1 to neutral and 100 amps. from line #2 to neutral and not be drawing a total of 200 amps?
That depends on what you mean by "a total."
When each line is carrying 100a at 120v, the total can be looked at as 200a at 120v. No problem there. But, we're splitting that 200a in half because we're doubling the voltage. Each line only has to carry half of the total load.
That's why each line's load is only 100a.
Let's say we're supplying only 240v (L-L) loads. If they total to 100a, that means each line carries 100a, not 200a, right? In the hypothetically-balanced system with line-to-neutral loads, there's no neutral current, so it behaves the same way.
In other words . . .
100a @ 120v + 100a @ 120v = 100a @ 240v
OR
100a @ 120v + 100a @ 120v = 200a @ 120v
. . . but not both.
Now, if we had a balanced line-to-neutral load of 100a on each line, and at the same time, a line-to-line load of 100a, the total current on each line would be 200a, not 300a.
If line #1 has 60a, line #2 80a, and there's a line-to-line of 50a, then L1 = 110a, L2 = 130a, and neutral = 20a.
Is that a better explanation?