gorms400

Member
I'm currently working on a cold storage freezer warehouse, 100k sq ft of -10 to 0 degrees F. We are installing conventional 400w high bays for general lighting, I'm trying to find/talk the owner into some battery backup lighting to take care of emergency lighting. We pulled a constant 277v circuit to every fixture location in case of this. No generator on site, so it's either a battery backup fixture or pipe a whole bunch of remote heads from battery units in the electric room. Has anyone seen a battery backup high bay that works in these temperatures?

FWIW the freezer is already getting down to around freezing for the next few days, poor planning, so that's why I suggested an LED or induction lamp high bay with backup capabilities. Thanks for any suggestions!
 
Last edited:

Barbqranch

Senior Member
Location
Arcata, CA
Occupation
Plant maintenance electrician Semi-retired
Not the same situation, but I was involved w/ a battery backup burglar alarm in an unheated building where 1 and 2 day power outages were common. Only way we could keep battery power w/o a huge battery was an insulated, heated (to 65 degrees F) box. Rechargeable batteries really lose capacity in low temperatures.
 

gorms400

Member
I've seen 2 head units before with a little heating pad right under the battery made for "unheated" areas so I wasn't sure if they made something like that for a high bay light, even if it was a t5 or LED. Looks like we're going to use remote heads and battery units in the machine room and spread out remote heads over the 100k sq ft, which I'm not crazy about.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Looks like we're going to use remote heads and battery units in the machine room and spread out remote heads over the 100k sq ft, which I'm not crazy about.
If the remote head wiring is 12V, be sure to do a voltage drop calculation, since the low voltage DC is more sensitive to a drop of the same number of volts than system AC voltage circuits are.
For a run of several hundred feet you may need some pretty big wire, especially if you are trunking the DC and then splitting it to individual heads.
 