How are you inspecting CEE

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
TN, kicking and screaming, is being drawn into the '08 Code (with ammendments) after many years on the '02.
There is a lot of controversy concerning CEE inspections. Some of the local jurisdictions have been enforcing CEE rules and allowing building (footer) inspectors to certify the steel is correct an allow a re-bar "stub-out".
Others have propesd it's an electrical connection and must be inspected by an electrical inspector.
I would appredciate input as to the requirements other agencies have on this inspection and what they are doing if the footer is completed without this being adddressed.
 
Electrical permit must be pulled and the CEE must be looked at and signed off before the builder can pour concrete.

CEE_Page_1.jpg


CEE_Page_2.jpg
 
In Utah, we have combination inspectors. I insepct the footing for structural steel placement and at the same time check it off as a CEE and make a note as to where the rebar stub is or where the copper conductor is located.

Chris
 
Here the building inspector checks the CEE during the footing inspection. IMO if you are smart enough to inspect an entire building you certainly can inspect a CEE.
 
Under FS 468 (Florida), only a licensed electrical inspector can approve electrical components and installations, including grounding electrodes. When the connection is to be made to a concrete encased rebar, it is typcial to allow the licensed building inspector to verify the rebar size, length, and location, with the conductor termination to it inspected by the EI at some other point in time.

In no case should a building inspector be approving the electrical installations themselves. And it really should not be the rebar / concrete contractor making the installation. (realizing it is happening all the time)
 
Do the EI's inspect water pipe used as electrode?

If it is rebar, then maybe a building inspector can manage...

If you use copper wire, then I guess it becomes more obvious an EI should be involved...
 
Even if it means purchaseing an additional permit. I think it should be inspected by an EI(some areas in TN do not have any building codes) I also think the EC's should be installing/connecting them. I am curious to see how TN decides to handle it.
 
They look for BD connectors and get in there to make sure the connection is tight? Here the EI's do.


Did you mean DB (direct burial) connectors? I honestly don't know what they do since I'm never around for a footing inspection by the building inspector. I'm sure that he does whatever the EI would do.
 
does the copper ground wire leaving the bottom or side of the footer require a sleeve of
any type as it travels the 8 inches through the concreate to the dirt and up into the service.
 
Under FS 468 (Florida), only a licensed electrical inspector can approve electrical components and installations, including grounding electrodes. When the connection is to be made to a concrete encased rebar, it is typcial to allow the licensed building inspector to verify the rebar size, length, and location, with the conductor termination to it inspected by the EI at some other point in time.

In no case should a building inspector be approving the electrical installations themselves. And it really should not be the rebar / concrete contractor making the installation. (realizing it is happening all the time)

Ditto.....
 
CEE location

CEE location

does the copper ground wire leaving the bottom or side of the footer require a sleeve of
any type as it travels the 8 inches through the concreate to the dirt and up into the service.

Ablue,

The CEE copper electrode ground must be contained by 2" encasement both horizontally and vertically until it exits above the foundation concrete. [250.52(A)(3)] Encased
 
In the jurisdiction I work for if the EC has not had a inspection of the CEE we ask for a letter from an engineer verifying it. The letter must be an original on letterhead with the the PE stamp.
 