How can fault current be calculated?

Status
Not open for further replies.
You need to start with the available fault current from the utility. Typically they will give you the fault current at the secondary terminals of thier transformer. You can use the calculations in post 2 to get the fault current at the line side of the service disconnect.
 
You need to start with the available fault current from the utility. Typically they will give you the fault current at the secondary terminals of thier transformer. You can use the calculations in post 2 to get the fault current at the line side of the service disconnect.

Thanks for mentioning the starting point :thumbsup:.
 
It would be interesting to see how these various calculations match with this measurement.


For 240v, if you have a 240v load that pulls 20A or so, you measure the 240 before and after turning off the load.
If the 240v increases by 0.5 volt when the load is switched off this source is capable of delivering 240v/(0.5v/20A) = 9.6 kA.
 