How close can underground conduits encased in concrete be to a fire hydrant?

Status
Not open for further replies.

Mitchum

Member
Location
California
Occupation
electrical inspector
I have underground conduits that will be encased in concrete. They are currently 5" away from a fire hydrant. The conduits will rise out of the ground next to the hydrant. Is this a code violation?
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I have underground conduits that will be encased in concrete. They are currently 5" away from a fire hydrant. The conduits will rise out of the ground next to the hydrant. Is this a code violation?
It might obstruct access to the hydrant. I have a hard time believing that is a good idea.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I have underground conduits that will be encased in concrete. They are currently 5" away from a fire hydrant. The conduits will rise out of the ground next to the hydrant. Is this a code violation?
If this is a true fire hydrant, then NFPA 1 will be your go to.
Generally 36” clearance is required unless AHJ approved less.
XFs have to be 48” away.
 