How come u can't run a single phase in each conduit in parallel feeds?
Seems like it'd actually be safer as there is no possibility of line to line short. I'm just thinking of make up in big mdp's. Is this just to keep the distance of each phase as equal as possible? It seems if u run all your pvc close enough you'd be within 3ft on makeup.
You can't do it with metallic conduit, because induced magnetic fields will induce currents in the conduits that will make them get hot, not unlike an old-fashion transformer-based soldering gun.
You can do it with PVC, but you need to cut slots between every knockout involved with the group, at each end, in each metal enclosure, effectively creating one large opening in the metal.
Ok most of ours are pvc anyways so if u are coming straight up into it with just pvc cut off at the slab is that ok?
You could also leave out the metal plate at the bottom of the enclosure. 🙂
My understanding is that the big restriction is on ferromagnetic metal (steel and such).
You have to run an EGC in each conduit (if this is a feeder and an EGC is required), and presumably you will see circulating current in all of the parallel EGCs. But unless I am mistaken code _requires_ this, and I've not heard that it is a problem.
-Jon
In most situations, you do not count the neutral as a CCC. Say you have 4 conduits with a phase in each conduit:
HHHNG, HHHNG, HHHNG, HHHNG
You have 3 CCC in each of 4 conduits.
Now change to isolated phase:
HHHHG, HHHHG, HHHHG, NNNNG
Now you have 4CCC in each of 3 conduits, and 1 conduit with no CCC.
Depending upon the size of the neutral relative to the phase conductors, if you have oversized conductors for voltage drop, if you are using 75C or 90C terminations, this may or may not make a difference.
-Jon
Agreed, they actually have current flowing in them, but they don't _count_ as 'current carrying conductors' for purpose of derating.
Physics-wise, that clearly only applies when one conduit has a full boat. I.e. L1, L2, L3, and N together can only be 3 simultaneous CCCs. Separate those out into separate conduits, and all 4 N can be carrying current at once, and that conduit has 4 CCCs, not 0 CCCs.
The NEC language on this point may be lacking, but that would be an oversight in the NEC.
Cheers, Wayne
They do when current they carry does not reduce current in other conductors in the same conduit.
Load up any one phase, and the neutrals will have to carry the same current in a different conduit.
Those currents are not subtractive, which is why this thread about phase isolation is taking place.