hi everybody! i'm new here but have been pursuing a career in the electrical field for a number of years. i have come across a problem that for the life of me i can't figure out or maybe i just don't know how to word my question. so here it goes.......
i have a 225 KVA DELTA transformer that feeds a three phase panel. the voltage is 240 volt. it is a true DELTA. no neutral.
the panel is rated for 800 amps but is protected by a 600 amp fused disconnect.
the name plate on the transformer and my math both come up with 540 amp capacity. ( 225000/240*1.73) so far everything is good.
the problem is that i want to add another circuit to this panel but cant figure out the theory on how it is loaded now and how much load can still be added safely. the breakers are as follows
quantity 1 3 phase 80 amp breaker
quantity 8 3 phase 60 amp breaker
quantity 6 3 phase 30 amp breaker
all these loads are continuous duty as they run machines that never shut down and if i calculate for worse case scenario i would add all the breakers and multiply by .80 coming up with 592 amps.
when i take an actual amp reading on the feeders it is but a fraction of the capacity, when i do the math it would suggest that something should be on fire!
please help :?
i have a 225 KVA DELTA transformer that feeds a three phase panel. the voltage is 240 volt. it is a true DELTA. no neutral.
the panel is rated for 800 amps but is protected by a 600 amp fused disconnect.
the name plate on the transformer and my math both come up with 540 amp capacity. ( 225000/240*1.73) so far everything is good.
the problem is that i want to add another circuit to this panel but cant figure out the theory on how it is loaded now and how much load can still be added safely. the breakers are as follows
quantity 1 3 phase 80 amp breaker
quantity 8 3 phase 60 amp breaker
quantity 6 3 phase 30 amp breaker
all these loads are continuous duty as they run machines that never shut down and if i calculate for worse case scenario i would add all the breakers and multiply by .80 coming up with 592 amps.
when i take an actual amp reading on the feeders it is but a fraction of the capacity, when i do the math it would suggest that something should be on fire!
please help :?