The circuit is 100A, 480VAC 3 phase, protected with a 100A breaker feeding #3 THHN, then to a junction box transitioning to a drop cord.
In the past (for smaller 30 amp drops) I've used table 310.15(B)(16) for the THHN and table 400.5(A) for the cord. Table 400.5(A) only goes up to #2 with column A highest rating of 80 amps.
What table do I use to figure the proper size cord for my 100 A requirements?
In the past (for smaller 30 amp drops) I've used table 310.15(B)(16) for the THHN and table 400.5(A) for the cord. Table 400.5(A) only goes up to #2 with column A highest rating of 80 amps.
What table do I use to figure the proper size cord for my 100 A requirements?