Hi guys,
I'm looking at the code in order to run TC-ER cable on top of cable tray. This will be running from a non classified area to a class 1 div 2 area in order to terminate on a motor (controlled by a VFD).
The VFD cable I'm looking at the moment is a 3/C with a ground wire per phase, type TC-ER for VFDs. Now, this does not have a gas/vapor tight sheath but it is rated for C1/D2.
Looking at the 2017 code 510.15(E)(4) where it mentions that a cable without this sheath needs to sealed at the boundary between unclassified and c1/d2.
(4) Cables Without Gas/Vaportight Sheath. Cables that do
not have a gas/vaportight continuous sheath shall be sealed at
the boundary of the Division 2 and unclassified location in such
a manner as to minimize the passage of gases or vapors into an
unclassified location.
How do I do this with a multiconductor cable or even a single conductor cable on a cable tray?
Thanks
I'm looking at the code in order to run TC-ER cable on top of cable tray. This will be running from a non classified area to a class 1 div 2 area in order to terminate on a motor (controlled by a VFD).
The VFD cable I'm looking at the moment is a 3/C with a ground wire per phase, type TC-ER for VFDs. Now, this does not have a gas/vapor tight sheath but it is rated for C1/D2.
Looking at the 2017 code 510.15(E)(4) where it mentions that a cable without this sheath needs to sealed at the boundary between unclassified and c1/d2.
(4) Cables Without Gas/Vaportight Sheath. Cables that do
not have a gas/vaportight continuous sheath shall be sealed at
the boundary of the Division 2 and unclassified location in such
a manner as to minimize the passage of gases or vapors into an
unclassified location.
How do I do this with a multiconductor cable or even a single conductor cable on a cable tray?
Thanks