How do i size this particular equipment (6I89T Edge Sander)

Cartoon1

Senior Member
Location
Florida
Occupation
Electrical Engineer
I'm confused on how to size this equipment 1.5 HP, 110 V, 18 amp. But it has a 15-5P plug. So do i do 20Amp circuit branch breaker and a dedicated receptacle or a 15amp branch breaker and a dedicated receptacle?

Thank you,
 
#1 What does the manufacture specify?
#2 Whats the nature of this load, that's not a continuous 18 amps or it wouldn't have a 5-15p on it?

Definitely a 20A circuit min.
Otherwise 18*1.25 = 22.5 Amps -> 25 amps breaker 10 awg wire. 5-30p
 
I'm confused on how to size this equipment 1.5 HP, 110 V, 18 amp.
15 amp plug from the manufacturer means that it should run on a 15 amp circuit. My guess is that the 1.5HP rating is highly inflated. For 115 volts from NEC T430.248 a 1.5 HP motor has a FLC of 20 amps.
 