How do I supply 600V Equipment?
theophilus88
Professional Architectural Engineer
St. Louis, MO
I am working on a giant fruit and nut processing facility in Missouri, and the owner wants to reuse (2) pieces of equipment that require 600V's..... I have told him several times that this is not possible, but they insist on wanting this voltage since the equipment is too expensive to replace. Does anyone know the best way to supply 600V's to your building? The only idea I had was to provide another service entrance transformer for this equipment which would be incredibly expensive or some sort of step up transformer from 480V to 600V. Does this even exist? Thanks in advance for any information.
Step up from 480 to 600 definitely exists, although the particular size you need may be special order.
Does the equipment require three phase with 600 volts line to line? Does it require a neutral?
To avoid grounding problems (some equipment does not like corner ground), be sure to specify delta (or wye with neutral point floating) primary and wye secondary, even if the equipment only needs 3 wires.
One option is an auto transformer.
Over the years I've done a number of 600-volt jobs but they all had 600 volts coming in from the utility. I don't see why you couldn't get a 480 to 600 V transformer of some sort unless the current draw is just so huge that it's not worth the effort. You might be able to get the utility to drop a 600-volt service in for you if it's big enough to require it
But they might bill you for the cost of their transformer. :(
In the past I have used autotransformer a to feed 600V panels and busway systems. It is not a big deal. I never even considered a second setvice.
Decades ago I field assembled a bank using standard 480:120V single phase units, but I don't think the manufacturer approves that connection anymore.
600V three phase was common in Ontario when I was working up there, so Canada might be a source of used transformers to do the job you need.
It is certainly possible to get 600V if you have 480V available, and the above posts describe several ways to do it (New service from utility, delta:wye step up transformer, autotransformer, bank of standard transformers).
Which of these is 'best' depends upon lots of details that you've not provided, such as how many kVA the equipment requires, if there are starting/inrush loads which must be supplied, if the equipment requires a balanced 3 phase supply (600V L-L _and_ 346V L-N (or L-G), etc.)
-Jon
A delta-wye step up transformer has the advantage that it provides some isolation to noise, and it also reduces the level of certain harmonic currents due to the load at the transformer line inputs. A delta-wye also typically has several primary taps that can accommodate some offset and imbalance in the line input voltages.
An autotransformer will be significantly less costly and smaller for a 480V to 600V step-up than a delta-wye. It will also will draw less current under a no-load condition. However, autotransformers often will not have taps for fine adjustments, and they provide negligible isolation to noise and harmonics.
Here are some examples of 480V to 600V step up transformers and an autotransformer, but many other kVA ratings are available:
I think somewhere we still have a transformer bank for making 600 volts out of 208 for testing VFD panels when we are making a bunch of 600 V units. But it was just enough power to do the initial smoke test.
Will you be allowed to have two voltages dropped to the building?
Maybe. Kind of depends on your situation and your utility. Most of them are pretty reasonable about such things if it makes sense. If you need 100 amps of 600 V though it is highly unlikely they are going to do it. If you need a thousand amps they probably would.
Textiles in the US south used a lot of 600V. The machinery OEM for whom I worked had 200 (208) as plant power. As some of the machinery had resistive elements and went to other countries, ours had a 200 primary with 240, 415, 460, and 575 outputs. This predated moderately priced VFDs which meant the 50Hz motors were not PROPERLY tested, but we just ran them under no-load for our pre-ship testing.