I am curious about the actual application of this new table, as it located in Part VIII of Article 240 and refers back to Part II.

Maybe Charlie Eldridge could help us (me) here, seeing he is one of the principles of CMP 10. Sorry Charles, I hope I am not putting you on the spot.
 
First off this is in a part of the Article that is for "supervised industrial locations", and like the other parts of the code for that occupancy, it acts as an exception to the general rules. The section will let the engineer use a tap conductor that would be smaller than what would be required by the other parts of Article 240. The engineer would use the trip time for the OCPD on the line side of the tap conductor along with the formula in the table to find a conductor that will not be damaged by the increase in temperature caused by the short circuit current.
 
The following is part of the substantiation for proposal 10-21 that resulted in the table. Note that the original proposal was for section 240.21(B), but the CMP moved it to 240.92 so that it could only be used for supervised industrial applications
The existing NEC requirements for these feeder taps dictate that the ampacity of the secondary tap conductors be at least 1/3 of the overcurrent device protecting the feeder conductor multiplied by the primary-to-secondary voltage ratio. At first, this sizing seems reasonable when considering that the feeder circuit device is being asked to provide short-circuit protection for the smaller tap conductors. But, this is often extremely conservative and frequently results in a conductor sized much larger than is actually required according to the laws of physics. By using formulas that have been widely utilized by IEEE, the Canadian Electrical Code, and the IEC, much smaller conductors can be installed. This will provide significant cost savings for electrical distribution systems, allowing North American manufacturers to be more competitive in the global marketplace.
An example would be helpful. Assume a feeder conductor is a 3/0 with an ampacity of 200 amperes, and protected with a 200 ampere overcurrent protective device. Also assume a one-to-one voltage ratio for simplicity. According to the 2005 NEC, the smallest 25 foot secondary tap conductor would be a 4 AWG with an ampacity of 85 amperes, even if it were only supplying a 10 ampere load. (Three times the ampacity of a 6 AWG, with an ampacity of 65 only gives 195 amperes, which doesn?t meet the 200 ampere requirement.) According to the physics formula, and UL standards, a 200 ampere Class J fuse will protect a 10 AWG conductor for faults up to 200,000 amperes. (Maximum I 2 t let-through of a 200 ampere Class J fuse at 600 volts with 200,000 amperes available is 300 x 10 3 ampere squared seconds, while the short-circuit withstand of a 10AWG copper conductor is 303 x 10 3 ampere squared seconds.) As we can imagine the cost savings here will be substantial, and within the safety umbrella of internationally accepted standard physics formulas.
 