Hi I am an electrical designer. We do the load calculations according to the NEC to size the electrical equipment rating and determine the service conductors size. The utility company(PECO) is asking the client/us for a contract limit for PECO's High Tension service (13.2KV service) of a building we design. The contract limit is a KW demand. If the actual demand is less than 40% of the contract limit, the client will still be charged based on the 40% of the contract limit for the transmission.
The NEC calculated KVA/KW is overkilled for the actual KW demand. If we use the NEC calculated KW, there will be money loss for the client. But how do we estimate the actual KW demand to avoid money loss for the client but still reserve enough power from the utility power grid? Do you have any similar experience?
This building has 247 apartments, one CVS pharmacy and one Aldi supermarket. Who usually calculate/estimate the actual KW demand? Shall we ask the Aldi and CVS stores in the same area of the similar size for the actual demand?
Thank you!!
The NEC calculated KVA/KW is overkilled for the actual KW demand. If we use the NEC calculated KW, there will be money loss for the client. But how do we estimate the actual KW demand to avoid money loss for the client but still reserve enough power from the utility power grid? Do you have any similar experience?
This building has 247 apartments, one CVS pharmacy and one Aldi supermarket. Who usually calculate/estimate the actual KW demand? Shall we ask the Aldi and CVS stores in the same area of the similar size for the actual demand?