Re: How do you find neutral current in a single phase system
Wayne, that brings up another use of the clamp-on. If you find a suspicious circuit you can clamp around the individual conductors and then around pairs. This will tell you if you have two L-1s together. Also, sometimes the wrong neutral is run with a hot, so comparing individual readings with pairs shows you when you have a neutral with the wrong phase (from another circuit). It adds instead of subtracts. Two-phase is fun too.
Recently I clamped around a romex. Zero, as it should be. But when I clamped around the hot it was zero, the neutral was 4.18A, and the EGC was 4.18A. Obviously the neutral and ground were at oposite phase angles since they read zero together. So the only logical answer was that the neutral ran down the cable to where it was connected to the grounding conductor, which then brought it back to (in this case) the junction box, then building steel, then a copper pipe, and back to the Tformer. Fun and games with a clamp-on. (Need a mini for some of this).
Karl