In an existing installation, sometimes you don't know.When connecting to building steel or water pipe, how do you know if these are properly grounded electrodes so that you can continue to use them as such?
You might be able to use an ohm meter to check resistance of grounding electrode conductors from one end to the other, but it will not help you to determine if a grounding electrode or grounding electrode system is effective.Ohm meter?
But at same time "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present" must be used - it doesn't mention testing them to see how effective they may be, other then later mentioning supplementing rod, pipe or plate electrodes that are over 25 ohms.When in doubt, it's always easier just to drive two ground rods and not go through all the hassle of trying to verify existing electrodes. The FOP test will only give you a resistance value, it won't tell you if the building steel or water pipe meet NEC requirements for contact distances. A water pipe with only 4 feet of metal to earth contact isn't an NEC electrode no matter how low the FOP values are.
I've always just done it and not worried about it. Water pipes are a bit of a worry with plastic becoming more common, never seen it used in a commercial building yet though. I never give building steel a second thought.When connecting to building steel or water pipe, how do you know if these are properly grounded electrodes so that you can continue to use them as such?