How do you size a service that will have 2 - 800a and 1 - 400a breaker

Status
Not open for further replies.
We are swapping out 3 Ats and i wanted to set up a temporary panel that can handle the load of all three . There are 2 - 800a and 1 - 100 a Ats. Do i just add them up and size my feeders from the total amperage? Any help would be appreciated. Thanks
 
Generally adding breaker/feeder sizes will result in a much larger than necessary system. Not sure if these loads you are talking about constitute the whole service, but if they do, how about getting demand data from the utility?
 

kwired

Electron manager
Location
NE Nebraska
Just because you have an 800 amp breaker doesn't mean it sees 800 amp of load. On top of that you indicate this is for temporary purposes, I'd be looking even harder at what the actual load will be during the use of this temporary setup.

As mentioned if legally required standby or healthcare those can complicate things easily.
 