75hp 480V 3ph fire pump is directly connected to the secondary side of utility xfmr. Then the secondary conductors go from xfmr to the listed fire pump controller. Here is what I would size EGC for the fire pump but I am not so convinced.
1) From Xfmr to the listed fire pump controller
75 hp FLA=96A
96*1.25=120A #1 AWG
Per 250.30A(2) and 250.102(C), EGC is #6 AWG ??
Is it really Equipmnet bonding jumper? I am confused here as well because this is not a SDS, it is a service.
2) From the listed fire pump controller to the fire pump.
I am lost here. Per 250.122(D), EGC size is permitted to be based on the rating of the motor overload protective device. But 695.6(D) prohibits automatic protection against overloads. So, how you you size the EGC? Do I assume there will be overload protection and size EGC based on that? (Which would be #6 AWG). Or do I extend EGC from the xfmr to the controller to the fire pump as well?
Thank you for your answers in advance.
1) From Xfmr to the listed fire pump controller
75 hp FLA=96A
96*1.25=120A #1 AWG
Per 250.30A(2) and 250.102(C), EGC is #6 AWG ??
Is it really Equipmnet bonding jumper? I am confused here as well because this is not a SDS, it is a service.
2) From the listed fire pump controller to the fire pump.
I am lost here. Per 250.122(D), EGC size is permitted to be based on the rating of the motor overload protective device. But 695.6(D) prohibits automatic protection against overloads. So, how you you size the EGC? Do I assume there will be overload protection and size EGC based on that? (Which would be #6 AWG). Or do I extend EGC from the xfmr to the controller to the fire pump as well?