vladimirRM
Member
- Location
- Philippines
how do you size current transformers for protection and metering for 138kV substation?
how do you size current transformers for protection and metering for 138kV substation?
Maybe 138kV?What's the voltage,
You will most likely need both metering accuracy and relaying accuracy CTs but an extended range transformer might work depending on what you are doing. The metering CTs will be accurate at low current readings but will probably saturate for fault conditions. The relaying CTs will be sized to not saturate for available fault current but probably will not be accurate enough for low load currents (if metering for revenue).how do you size current transformers for protection and metering for 138kV substation?
Yes, another instance where the OP tells you as little as possible and everybody guesses what the real question is. You must be a soothsayer to have guessed 138kv out of the clear blue sky, a voltage that is a utility voltage unless you a dealing with an extremely large industrial facility with a 138kv service. Needless to say I'm impressed.Maybe 138kV?
and has a penchant for reading...You must be a soothsayer to have guessed 138kv out of the clear blue sky
how do you size current transformers for protection and metering for 138kV substation?
how do you size current transformers for protection and metering for 138kV substation?
If the CT is going round a 138kV bus bar I meant, then it would have to be adequately rated for that application.the voltage is 138kv, for protection and metering purposes
Unless you are asking just for your own curiosity, I would highly recommend you contact an engineering firm knowledgeable in HV substation design.
Some additional reading material:
http://www05.abb.com/global/scot/sc...7b130057ba48/$file/138000 section_updated.pdf
I imagined something like the one mentioned in this thread:If the CT is going round a 138kV bus bar I meant, then it would have to be adequately rated for that application.