If it has a neutral it could be a delta/high leg system.Where it matters is at the incoming service transformer. If THAT transformer has a Neutral, it's a Wye secondary.
Yep. Simplest way is usually the best way.Where it matters is at the incoming service transformer. If THAT transformer has a Neutral, it's a Wye secondary. But if you can get that far into it, you can likely just read the nameplate to see it anyway.
OP is apparently in Canada - 600 volts is common there, don't know if they commonly have 600 volts from a delta secondary or not though. Wye system would be 600/347 volts. A 600 volt delta with high leg would be 300 to neutral on two lines and about 520 on the high leg.Let's talk lower voltage for a minute... 208V and 240V.
If you get a look at the wires and they are colored or taped black, red, blue and white, by convention (not code) that's supposed to be 208/120 wye. If there's no pattern to how the breakers in a panel are installed, then it's almost certainly that.
If you open a panel and you notice either:
- every third space is missing a breaker (unless it's got 1-pole of a three pole breaker)
- a wire taped orange instead of blue (or purple instead of blue in San Francisco)
then that is probably a high leg delta. Black and red should be ~120V to neutral, and orange (or purple) should be ~208V. That's why there's no single pole breakers in those spaces.
I've never personally seen an ungrounded or corner grounded delta, but those will not have a neutral.
Now if the voltage is 600 and you don't have much experience knowing your services then you should look for a label or ask someone else.
We are sub metering a building a was asked whether the 600V 400A service was delta or wye and I have no idea... any help is appreciated!
If it has a neutral it could be a delta/high leg system.
OK, but I was addressing what appeared to me to be a global comment that if it's three phase with a neutral it must be a wye.Context. The likelihood of a 600V delta high leg system with a center tapped winding where the L-N is 300V... not quite even approaching a hint of being slim, to none.
OK, but I was addressing what appeared to me to be a global comment that if it's three phase with a neutral it must be a wye.
If it has a neutral it could be a delta/high leg system.
See post #11The OP is from Ontario Canada. Ive never seen a high leg system in Canada
You should go, it's pretty up there. Don't bother with Manitoba and Saskatchewan, they will look exactly like home to you, but I love Banff and Lake Louise in the Rockies. A trip on "The One" (Hwy 1) from Calgary to Vancouver in a good car is one of the all time great road trips. It's also a nice train ride.I've never seen any system in Canada![]()