How does Con Edison afford this?

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Small strip mall fed with a 2x service. 2 separate aerial bundle circuits, tapped to dive underground. Each feeds an individual network transformer- both 480 volt secondaries in parallel. My question is, how does Con Edison afford two times the infrastructure for a single story building out in the boonies?
Typically this would be a one 3 phase URD with a few padmounts around the property.






 

Coppersmith

Senior Member
Location
Tampa, FL, USA
Occupation
Electrical Contractor
Aren't you forgetting the secret Government bunker hidden under the mall. It needs lots of power. Ooops. Never mind. Nothing to see here.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I think the more correct question would be "How can ConEd customers afford two times the infrastructure"?
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
All depends on the anticipated revenue over the first years after install. The POCO normally calculates that based on the load info. provided by the customer. The POCO will credit some some percentage of that for the install off the installation cost.

The rest (anything above and beyond the credit) is all on the customer. For all we know, the customer completely paid for the second transformer and install.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
All depends on the anticipated revenue over the first years after install. The POCO normally calculates that based on the load info. provided by the customer. The POCO will credit some some percentage of that for the install off the installation cost.

The rest (anything above and beyond the credit) is all on the customer. For all we know, the customer completely paid for the second transformer and install.

I guess a lot of customers like paying for their second transformer 😜
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Its obviously not that anyone wants to pay more than they have to.:)

But if you can get redundancy by having the POCO provide 2 transformers and 2 primary feeds, it may be worth the added cost to some clients.

With an AHJ approval and some attention to detail (including the 10 second transfer rule), that second utility feed can even be an emergency source.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Couple of questions.. how do you know both XFs are 480?

I see one circuit with bare wire, and two circuits with UG wire bundled overhead.

a triple circuit pole would take a lot of height to meet clearances.
I don’t know how far out in the boonies they are, but we used to have UG wires bundled like that for clearances in a downtown area until the city had a MAJOR infrastructure overhaul, it was then we buried the wire and got it out of the air While the street was torn to pieces.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Couple of questions.. how do you know both XFs are 480?

I see one circuit with bare wire, and two circuits with UG wire bundled overhead.

a triple circuit pole would take a lot of height to meet clearances.
I don’t know how far out in the boonies they are, but we used to have UG wires bundled like that for clearances in a downtown area until the city had a MAJOR infrastructure overhaul, it was then we buried the wire and got it out of the air While the street was torn to pieces.


480 is what the building uses and I see no MV secondary. Typically Con Ed will plop down a network transformer and run the secondaries into a collector bus (often in a vault) and then feed to the customer.

Poles are average height in this case.

Some POCOs will run bundled MV for extra circuits from one pole and/or reliability.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
480 is what the building uses and I see no MV secondary. Typically Con Ed will plop down a network transformer and run the secondaries into a collector bus (often in a vault) and then feed to the customer.

Poles are average height in this case.

Some POCOs will run bundled MV for extra circuits from one pole and/or reliability.
But how do you KNOW there isn’t some 208Y120 there?
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Couple of questions.. how do you know both XFs are 480?

I see one circuit with bare wire, and two circuits with UG wire bundled overhead.

a triple circuit pole would take a lot of height to meet clearances.
I don’t know how far out in the boonies they are, but we used to have UG wires bundled like that for clearances in a downtown area until the city had a MAJOR infrastructure overhaul, it was then we buried the wire and got it out of the air While the street was torn to pieces.
I was about to say the same thing, I know of a big box flooring store in Chattanooga TN that has two pad mounts, one for 277/480, the other for 120/208. The problem is, or was, both gears are rated for 120/208! We were quoting putting in the correct gear. I think the inspector caught it, but allowed them to open anyway. Looked like it had been that way for quite a few years.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I was about to say the same thing, I know of a big box flooring store in Chattanooga TN that has two pad mounts, one for 277/480, the other for 120/208. The problem is, or was, both gears are rated for 120/208! We were quoting putting in the correct gear. I think the inspector caught it, but allowed them to open anyway. Looked like it had been that way for quite a few years.


Depending on the available fault current there may not be any hazard. 120/208Y gear is frequently used on 240/416Y systems over seas.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
The rest (anything above and beyond the credit) is all on the customer. For all we know, the customer completely paid for the second transformer and install.


I think you mean customers - as there are many, many customers including Stop and Shops, Home Depots, officer buildings ect being fed with two transformers and two circuits.
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I think you mean customers - as there are many, many customers including Stop and Shops, Home Depots, officer buildings ect being fed with two transformers and two circuits.
Sounds like two voltages.
stop and shops don’t need 277/480.
Home Depot heat and air system might like 277/480 better.
 