Cinder_Electric
Member
ARTICLE 230.70.(A)1 states that a disconnect shall be installed at the nearest point of entrance.
ARTICLE 230.71(A) states that you can have up to six disconnects as long as they are all grouped on one location.
We installed a 200 amp panel service off a CT inside a indsutrial building. The CT was within 2 ft of the nearest point of entry. Our panel is roughly 7 ft away from the nearest point of entry and aprox 3-4 ft away from the CT. We received a violation saying that our panel was not at the nearest point of entrance and we have to now install a main 400 amp disconnect on the load side of the CT. There are currently less than 6 mains and they are all grouped in the same area. Do any professionals or inspectors have any comment on this situation. I would definetly appreciate some input.