I don't understand the question. MV is no different than LV, in the concept of sizing conductors. First you calculate the load, then you select a conductor that has sufficient ampacity for that load, then you select an overcurrent device capable of protecting that conductor against overcurrent. If necessary, you insert a step to check for voltage drop, and adjust the conductor size accordingly. What is it that you are asking for?
240----- covers LV cables
I. General
240.1 Scope. Parts I through VII of this article provide the general requirements for overcurrent protection and overcurrent protective devices not more than 600 volts, nominal. Part VIII covers overcurrent protection for those portions of supervised industrial installations operating at voltages of not more than 600 volts, nominal. Part IX covers overcurrent protection over 600 volts, nominal.