How (if?) the generator output can be higher w/ less excitation voltage?

Status
Not open for further replies.

moonshineJ

Member
Location
USA
The brushless exciter of a 3-phase motor-generator has (per manual) 2.61-3.19 Ω resistance of its stationary exciter field winding.

Exciter field voltage (no-load) is 23 VDC @ 5.7 A
Exciter field voltage (full load) is 25 VDC @ 6.25 A

The rated output voltage is 3-phase, 120 VAC, 400 Hz

After someone did repairs on the generator (one of 6 diodes of the rotating rectifier was blown), the generator output was 150 VAC (instead of its rated 120 VAC), and could not be regulated. After I verified that nothing else is damaged (the wiring, the components inside the voltage regulator, etc.), I started the MG and the output of generator was 150 VAC.Motor runs at its rated 1200 rpm, nothing else is wrong. I verified voltage shown by the cabinet voltmeter with my Fluke; still 150 VAC.

Here is the question: when I checked voltage going to exciter’s filed winding (F1, F2 terminals…sounds familiar?) I saw 13.3 VDC. I put clamp-on meter and it showed 7.7 going to the field. Yet, voltage output of the MG was 150 VAC (no control), not 120 VAC. Also, I checked the resistance of stationary exciter field winding…3 Ω, which is perfectly good per tech manual.


Unfortunately, I was diverted to work on another MG set which also had a recent casualty. I replaced a blown motor starter with the one from the MG I was working initially on. Changed wiring, did all checks, then started the MGset. There was 150 VAC (no control) instead of 120 VAC. After some playing withthe voltage regulator, I made it to work. Due to no parts for another MG set, I could not continue work on it.

A few weeks later other folks installed a new motor starter (instead of the one which I used on another MG), and replaced the whole voltage regulator, having fixed the problem with unregulated 150 VAC.

Since it was repaired, and I was not there, I could not replicate the problem and figure out how 13.3 VDC @ 7.7 A going to the field would buildup 150 VAC instead of 120 VAC. When I called the company, and asked how this is possible, they tried to say that by the Ohms law I should have the low resistance of the exciter’s field winding. But it was not 1.8 Ω (per G. Ohm), but 3 Ω (and later on this MG was fixed merely by replacing the whole voltage regulator).

The only one thing I could think of, was a situation which I saw a couple of times with AC power distribution. When 115 VAC (hot and neutral) has a hot wire touching a ground somewhere (I believe there was water intrusion into HOT wire of 115 VAC underwater cable), I saw hot wire having half of 120 VAC. Replacing the cable fixed the problem. Here, with the MG, I saw 13 VDC, which is roughly half of 23-25 VDC required to build the rated output.

I’m still really puzzled; any ideas?
 
Last edited:

moonshineJ

Member
Location
USA
Phil,
unfortunately at that time I didn't take AC voltage and amp readings for the generator's exciter field winding. I used Fluke multimeter and Fluke clamp-on meter to take DC readings. I even didn't want to run the MG at 150 VAC longer than 10 or so seconds, because I didn't know what's going on at beginning. The guy who troubleshot it before sent me email, so I knew that one diode was replaced (I unwired each one and tested them individually just to be sure they are still all OK), and the output was 150 VAC, no control. I checked for grounds and resistances on all windings per manufacturer's manual - everything seemed to be OK. Visually inspected everything - no problems. Then I proceeded cautiously with run test and was taking readings on some test points within the VR.
Again, the folks decided that they want another MG get fixed, so I moved on on another one and ended up having no starter to fix the first one after I fixed the problem on the second one. The second one had also 150 VAC, no control, + it was tripping on overvoltage (it should kill the VR if the gen volts go pass 144 VAC). I also tried to take VDC readings, but digital Fluke has too much "inertia": during 1-1.5 before the VR would go off I saw that VDC go pass 13 VDC as on first MG. I could see some 15-16 VDC before the gen's VR would go off. I eventually made it to work messing with adjustment pots within the VR. It still doesn't explain how output VAC go high with low VDC to the field..
Now they both run great, so I cannot take any AC readings anymore on the field wiring.
 
Last edited: