How large does a vertical chase need to be to run (8) 2-1/2" conduits between floors? Is there a general calculation for x number of y size conduits? How do we account for working space?
Thank you.
 
I've tried to solve this before on projects by finding the outter diameter of the conduit, then using a conduit spacing chart, draw the most efficient chase size based on your conduit spacing.
 
What type of conduit and what is your spacing? You can probably go as little as 3/4" of an inch between each conduit. 2.5" metal conduits are about 3" in diameter.
(3"*8)+(3/4"*7)=29 ¼"
 
Not sure how the conduits terminate but to avoid having to bend offsets keep your locknut & bushing dimensions in mind.
(Learned from my own error...punch holes based on conduit and then can't get fitting on easily)
 
Not sure how the conduits terminate but to avoid having to bend offsets keep your locknut & bushing dimensions in mind.
(Learned from my own error...punch holes based on conduit and then can't get fitting on easily)
Agreed! It's no fun when your locknuts mesh like gears. :rolleyes:
 
Maybe trying to figure out the smallest chase isn't the right approach. The pipe installers will be happier with some room to work with vs. not.
I agree, we use 1.5" spacing with 4" conduits. For 2½" EMT 3/4" will still work.
 
You’re right if the conduits are for data they would be a waste of money if it’s for power it’s cheaper. You would be surprised how cheep buss duct is and how much current it can carry for the cost
At what amperage does bus duct make sense? If I have 225A bus duct feeding panels on 5 floors, is it cost effective? From my call w/ a rep, currently there's a lead time of 6 months, plus higher metal costs, plus it requires on-site measurements to custom the bus duct, etc.
Thanks.
 
infinity,
Thanks for the answer. Is there a chart somewhere to look this up?

Not that I know of. 1.5" spacing is all that you would need if you wanted to go with the larger size. If room is tight you could shrink the spaces down but if you use 1.5" you won't have any issues with connectors or locknuts/bushings, etc.
 