I have a question about the NEC. I will be feeding a fire pump controller from a new transformer that is remote from a building. I understand that I cannot put overcurrent protection on the secondary side of the transformer. This gives me a 90' run from the transformer to the overcurrent protection which is at the fire pump controller. How far can this run be?
 
The relevant code sections:
 
695.5(B) Prohibits overcurrent protection on the secondary before the fire pump controller.
 
240.4 (F) Informs me that the wires on the secondary side of my delta-wye transformer cannot be assumed to be protected by the primary fuses.
 
Okay, so that seems to indicate that I have a section of conductors that are protected only by the fuses at the controller (on the load side of the conductors). That naturally brings me to section 240.21. Here I get stuck.
 
240.21(B)(5) seems to say my conductors can be unlimited outside the building. But I cannot use this rule because it requires that the conductors must end at a single circuit breaker or fuse. (I feed two sets of overcurrent protection, the main pump and the jockey pump.) Further, I would need to locate my controller where the conductors enter the building, which is physically impossible.
 
I seem to be ending up at 240.21(B)(1) which limits me to 10 foot total conductor length. That is way too short.
 
Can anybody help me? I would love to hear your comments.
	
		
			
		
		
	
				
			The relevant code sections:
695.5(B) Prohibits overcurrent protection on the secondary before the fire pump controller.
240.4 (F) Informs me that the wires on the secondary side of my delta-wye transformer cannot be assumed to be protected by the primary fuses.
Okay, so that seems to indicate that I have a section of conductors that are protected only by the fuses at the controller (on the load side of the conductors). That naturally brings me to section 240.21. Here I get stuck.
240.21(B)(5) seems to say my conductors can be unlimited outside the building. But I cannot use this rule because it requires that the conductors must end at a single circuit breaker or fuse. (I feed two sets of overcurrent protection, the main pump and the jockey pump.) Further, I would need to locate my controller where the conductors enter the building, which is physically impossible.
I seem to be ending up at 240.21(B)(1) which limits me to 10 foot total conductor length. That is way too short.
Can anybody help me? I would love to hear your comments.
 
				
 
 
		