bill@usps06492
Member
- Location
- Connecticut
I want to know if my load calculation is correct,I have 4-125A circuits that I want to install in a 500A panel, but I think that the max I can do is only 3-125A ckts(everything is 3phase 208/120V). 125Ax208Vx1.73=44980VA 44980VAx4=179,920VA 500Ax208Vx1.73=179,980VA 179,980x80%=143,936VA 143,936VA/208Vx1.73=400A 44,980VAx3=134,940VA. The load being servered is in an industrial environment,so do I have to be concerned with loading the panel over 80%,can I rate it at 100%? All the equipment will run at the same time, and the maximum run time is about two hours of steady running, and the actual Amp draw when running(minus start in rush) is less than 80% of the 125A ocpd.