If it's rated at 200 A, then 200 A it is. Unlikely that 201 A would trip it. And if it did, you'd need a calendar rather than a stop watch to get the time to trip.I was wondering how many amps would normally cause a 200 amp main breaker to trip. 201 yes. But is that 201 on each leg or 101 on each leg?
I infer you are talking about a single phase service. 201 amps flowing through the breaker means that 201 amps are on Phase A and 201 amps are on Phase B, for a "total" (I hate using that word in this context) of 201 amps. It is the same current that flows out of the breaker on one leg and back into the breaker on the other leg.But is that 201 on each leg or 101 on each leg?
Ambient temperature does factor into the trip time. Some of the previously mentioned loads and times do also have an ambient temp that goes with those ratings.It all depends on the conditions.
Anyone who says it will carry its rated amperage indefinitely has never been in charge of keeping the power on to a stage at an outdoor event with a fully loaded panel in 100 degree temperatures.
True.Yet none were mentioned.
True.
I believe most of those tests are done at 40 deg C.
Yes, but he also mentioned a situation of 201 amps on a 200 amp breaker. It can carry more then 200 amps, how much more and for how long depends on other factors and some of those have been mentioned. Or it could even trip on a load under 200 amps in a high ambient temperature, but time will also be a factor in that situation.I may be wrong, but without getting too technical,
It seems the OP was just trying to get a grasp on the common misconception that 100 amps on A Phase + 100 Amps on B Phase = 200 Amp Breaker that is at or near trip point.
Not so, It's only about half, or a little over half the way there.
The 200 Amp Breaker has the capability of handling 200 Amps per Phase.
I see two questions being asked.You can tell by the way he posed the question that he was simply inquiring if the breaker is looking at a combined total of both legs added together or each leg individually.
This is not JeopardyI see the 201A as not being given in the form of a question even though it should have been.