I am doing a fire station project. The entire fire station will be backed up by a generator. I thought only one ATS is needed after main breaker for the service and main breaker for the generator. I checked 700.6 of 2005 NEC handbook that says "If a single generator is used to supply both emergency and nonemergency loads, then multiple transfer switches are required" . So I have to use at least two ATS, one for emergency load such as emergency lights, the other for nonemergency load such as HVAC units. And I have to put four more disconnects for protecting the two ATS. Do I have to do it this way?
Any ideas will be appreciated.
David